G

Gixxerdan

I have just installed 3 new sockets in my house. Before putting power on I went round with my multimeter and checked the resistances between earth and neutral/live to check there was no shorts and all tested ok so went round with a 240v rated floodlight to check all of the sockets with the power on. Plugged in to the first double-worked but then plugged it in to the other side of the same double socket- rcd tripped! Now it trips everytime I try plug something in. Any ideas? Ive tried a couple of different equipment and have gone round checking for loose wires but now im stuck... help please!
 
To note for starters you are lacking the correct test equipment.. you would need to do an IR test, ELI test as well as a few other tests when commisioning your 3 new sockets.
More details; how have you added these sockets are they on their own circuit or have you linked to existing and if the latter how have you linked them?
 
Probably connected the neutral incorrectly.

A couple of pointers; firstly there's a good chance you won't see an insulation fault that might cause RCD tripping with a multimeter. Secondly a floodlight is an item that's specifically designed to shed a high intensity light over a large area. It falls very short of the mark as a circuit tester. You needs to test the loop impedance, earth impedance etc etc of the circuit as per the regulations. These tests are designed to ensure that the circuit is safe and won't cause injury to a user.

Edit, sorry for any repeated advice, there were no replies when i started typing :(
 
To note for starters you are lacking the correct test equipment.. you would need to do an IR test, ELI test as well as a few other tests when commisioning your 3 new sockets.
More details; how have you added these sockets are they on their own circuit or have you linked to existing and if the latter how have you linked them?
I have linked them in to the ring main for downstairs.
 
I have just installed 3 new sockets in my house. Before putting power on I went round with my multimeter and checked the resistances between earth and neutral/live to check there was no shorts and all tested ok so went round with a 240v rated floodlight to check all of the sockets with the power on. Plugged in to the first double-worked but then plugged it in to the other side of the same double socket- rcd tripped! Now it trips everytime I try plug something in. Any ideas? Ive tried a couple of different equipment and have gone round checking for loose wires but now im stuck... help please!

Tell us where you are I'm sure one of us can help you for a reasonable rate.
 
if the ring is existing and you only added 3 twins and you have correct polarity and you haven't altered anything else then maybe an isulation fault from a trapped cable or damaged cable when clipping etc.... this can hide itself until a load is added, even harder to find is if you have disturbed or trapped another circuit while doing your sockets, again it may only show itself when load is added to the circuit.

To explain this i had a callout to DIY job and where-ever he plugged in any load the front end rcd tripped... it also did it on lighting but only some of them.... turns out a trapped lighting feed was the fault but made itself known even if the sockets were loaded up.
 
Sorry should of said- i tried a couple of different sockets

It seams impossible to me for the same item to be used in a double socket and on one side it's ok and the other side it trips RCD try swapping the socket for one u know works both sides like an old one that is already in use ( the chances are slim but it could be a faulty batch) and how did u wire this socket a spur or extended the ring?
 
if the ring is existing and you only added 3 twins and you have correct polarity and you haven't altered anything else then maybe an isulation fault from a trapped cable or damaged cable when clipping etc.... this can hide itself until a load is added, even harder to find is if you have disturbed or trapped another circuit while doing your sockets, again it may only show itself when load is added to the circuit.

To explain this i had a callout to DIY job and where-ever he plugged in any load the front end rcd tripped... it also did it on lighting but only some of them.... turns out a trapped lighting feed was the fault but made itself known even if the sockets were loaded up.

Ive fixed some of the cables with cable clips but i definately not hit any with the nails- could these still be causing the issue?
 
It seams impossible to me for the same item to be used in a double socket and on one side it's ok and the other side it trips RCD try swapping the socket for one u know works both sides like an old one that is already in use ( the chances are slim but it could be a faulty batch) and how did u wire this socket a spur or extended the ring?
I extended the ring. It worked one side then tried the othet and it tripped. Now trips
all the time whichever socket i put the load on so thinking i must of disturbed something but all the connections seem sound and secure...
 
Try unscrewing all the sockets u have worked on today and pull them forward and try that I've had it before where cables get pressure faults from the neutral to the back box.
Let me know how u get on
 

Reply to RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
496
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top