Hi all.
Need some help,I fitted a new dual rcd board today and have problems with the RFC tripping the RCD. Test results for circuit are as follows, r1=.34, rn=.36, r2= .81 (r2 a little higher than expected but I think still o.k?) I.R= 10.6 M ohms.lower than I would like but still acceptable ( again I think?)
Connect circuit and energise and all is ok, start switching on appliances and RCD trips,I tried all appliances off and switching on one at a time hoping to find the fault but any combination can make it happen especially ones drawing a higher load.ie kettle or microwave. Disconnected all other circuits to eliminate borrowed or wrongly placed neutral, tried circuit on the other RCD but still trips. Any suggestions on the best way forward
 
EFLI tested at 1 socket tripped RCD, but was ok at another,this socket also gave me a higher R1+R2 than others but was fine at terminals on back of socket so I changed the socket but didnt check ZS at this socket afterwards, by this time by head was begining to hurt.
 
If you rule out borrowed neutral and appliance plugged in not leaking then it has to be a fault somewhere on the circuit.

The RCD is monitoring the phase and neutral so any imbalance will be picked up and the unit will trip.

My bets on a loose connection at a S/O or a jointbox which is causing the havoc.

I would honestly invest in a earth leakage clamp as it will save you time in the future IMO !

Double check all your tail connections in the CU just to be sure !
 

Reply to rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
Ok I’ll try this when I’m down
Replies
4
Views
395

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top