G

goldie

Hi guys. slighty baffled by this one.
Rcd tripping intermittently when 3x 16watt 2d lights are switched off at the wall switch. Carried out ins res tests... All ok. Lights turn on fine and only trips 2 out of 10 times when turning switch off. possibly inductance causing earth leakage??
 
1) Ramp Test
2) Check earth leakage
3) Could be the electronics in the lights themselves causing surges/spikes that is affecting the RCD

After Ramp test if it's border line on low 20mA I would change.

If you do have High Protective currents then it becomes a little more complcated, you could move the lights circuit onto a seperate RCBO.

Try for a temporary measure replace the light/lights with another type
 
I had a similar issue with a low energy lamp in a Class 1 fitting. Tripping the RCBO intermittently. All tests were ok; removed & replaced the lamp and no tripping in the last two weeks. TBH, not entirely clear what the problem was within the lamp, but presumambly the electronics leaking to earth for some reason.

Regards
 
Thanks guys.
At the mo i have replaced the fittings to gls type. Trail n error. tried ramp test rcd wont trip with 15 ma fault current at full load so dont think its a build up of leakage. also wondered obout capacitance from two way switch wire onto cpc. have had a similar problem with two way switching showing shimmering l.v lamp on landing.
 
Thanks guys.
At the mo i have replaced the fittings to gls type. Trail n error. tried ramp test rcd wont trip with 15 ma fault current at full load so dont think its a build up of leakage. also wondered obout capacitance from two way switch wire onto cpc. have had a similar problem with two way switching showing shimmering l.v lamp on landing.

Not sure what you mean their Goldie, but a ramp test is not that.

The ramp test will trip the RCD and it will show you how many mA it as taken to do so. So you hopefully get a reading as close to 30mA as possible, but normally anything between 22-27 mA would be expected.

That why on my original post I said if you get something like 20 mA you can think about changing it
 
Its an old robin. i know what test u mean but yes mine doesnt have that function only does one half of sine wave too. i had to compramise by running full load and putting 15 ma fault current to sre if there was any sign of leakage to earth.
 

Reply to rcd tripping? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Sounds like it didnt live up to its IP65 rating. If under warranty get Amazon to replace it.
Replies
5
Views
519
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top