Peter Woodford

Guys,

just had a call off a customer who i changed a fuse board for a week ago and has reported that when switching the tumble dryer on each time if trips the rcd. readings on RCD 36.4 x 1 and 14.0 x 5 would you suggest changing the RCD.

cheers
 
would i do this at 250v test and just connect to the ends of the plug

The IEE guidelines suggest 500V with L+N joined together, but for the sake of fault finding it wont hurt to test at 250 especially if it shows something up.

Does the RCD trip every time?

Maybe N+E swapped at the socket, and has only come to light since installing an RCD.

I once installed a load of 30mA RCD's that fed single phase machinery (via 16A sockets) and had a nightmare with nuisance tripping even though machines tested ok.

I swapped all the RCD's for 30mA Hager as they claim to have filters to eliminate unwanted tripping, and the problem was solved.
 
don't think it trips every time but only install last weekend but tripped once last week and once this week so far by the sound of it only when they use tumble dryer, do you mean test 250v on the piece of equipment
 
Last edited by a moderator:
had same problem not so long ago, turned out to be tumble dryer but was difficult to explain to client that since we had done work there tumble dryer now does not work with new installation
 
tumble dryers are prone to earth leakage when old either element or motor and sometimes mains supressor (big capacitor to filter mains), if you have any digital timers controls etc on yhis dryer dont do an insulation test :eek: as you may blow the circuit boards.
Disconnect the element then try it, disconnect the supressor if it has one and try it again but if you still have tripping out issues then disconnect the motor and insulation test seperately.
Always replace the back or top before testing as a sealed dryer is sometimes needed for the airflow over elements, dont run without motor connected as elements will overheat and be careful of capacitor/supressor as it holds a nasty charge after power is switched off.
 
Just joined the forum tonight so I hope this is the correct way to post.

I had a fault similar to this. The problem was the appliance and it was down to dampness within the tumble dryer. The tumble dryer was a condensing type and a member of the household had failed to empty the water tank which had at some time overflowed into the back of the dryer. The dryer would start OK but when the heating element was switched in to circuit the RCD would trip.
The problem was cleared by using a hairdryer to dry off the sensors in the back of the dryer. If I remember correctly it was a LG Tumble Dryer.
I would suggest the fault has been there before you changed out the fuse box and the RCD has correctly highlited a earth- neutral fault when the appliance is running. It possibly is faulty only when the timer switches in the heating element circuit.
 

Reply to RCD tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top