Hi all.

Can anyone tell me why an RCD would take more than 2 minutes to trip after the main supply circuit has been energised.

Will not reset immediately afterwards but will reset after 3 to 5 minutes of isolating the circuit.

This is with no loads connected. that is all MCB's switched off.

My supply is from a SWA cable connected into a fused switch incorporating a BS3036 60 Amp fuse. The cable run is approx 12mtrs from the meter and cut-out dissapearing into the wall cavity and reappearing upstars of a domestic property converted to an appartment.

Any expert help would be gatefully appreciated.
 
I will be back tomorrow with my tester and will be able to do some tests.

What is stumping me is the delay in tripping. which would or could be explained if the RCD were based on thermal aspect of overload and not imballance of current. any thoughts on that ?
 
It would be a guessing game.

You need to carry out all the dead tests tehn the live along with RCD tests in case its duff.

It wont be on the SWA IMO as this is only suppling the power to the RCD it does its job by protecting the load side for any earth imbalances.

It will be on your load side neutral to earth fault as you are only switching of the line conductors with the MCB's if it is a cct

Try taking out all of the neutrals and replace them one at a time until you get your tester.
 
Sorry to be a nuisance Tony. I'm getting abit confused here. You say the rcd works on an imballance of current in the Line and neutral wires. I'm clear with that.

If there is no current flowing supplied to the line conductors there is no current in the neutral conductors iether. so no imballance should occure if there is a potential route to earth from a short between earth and neutral. Is that right? The problem also occured when I removed all line conductors from each MCB not just switched off. Its been a long day so I may be talking giberish.
 
Experianced the same problem on a job last year only it took between 5 and fifteen mins to trip rcd, turned out to be water ingress a JB feeding spike in the garden causing low I/R on earth and neutral
 
I would test your rcd and also ramp test it - you could well have a dodgy rcd. If you can't get it to hold while testing try putting one that you are confident is working or another new one in. Rule that problem out before spending a lot of time elsewhere imo.
 

Reply to RCD Trips after two minutes ? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top