Newpark7
-
Hi all
Replaced 3 old fuseboards today with a Wylex HI CU, customer just bought the property and didn't want a PIR just replace the board, I warned of the possible pitfalls of which he accepted.
On removing old boards did a quick IR test between CPC and phase & neutral joined together on all circuits, all ok apart from Ground Floor lights & Sockets which were 0.38M & 0.12M respectively.
On powering up the new board the RCD trips not surprisingly straight away when the socket MCB is switched on, the lighting circuit only trips when any light switch on that circuit is switched on.
I have temp wired the sockets into a non RCD protected way for tonight because of freezer etc. I appreciate there are faults there but just wondered how you guys would recommend going about testing and locating the faults.
I did quickly connect each leg of the ring separately to the MCB one leg trips straight away, the other trips after approx 5 seconds.
I am going back tomorrow and any help would be great - thanks.
Mark
Replaced 3 old fuseboards today with a Wylex HI CU, customer just bought the property and didn't want a PIR just replace the board, I warned of the possible pitfalls of which he accepted.
On removing old boards did a quick IR test between CPC and phase & neutral joined together on all circuits, all ok apart from Ground Floor lights & Sockets which were 0.38M & 0.12M respectively.
On powering up the new board the RCD trips not surprisingly straight away when the socket MCB is switched on, the lighting circuit only trips when any light switch on that circuit is switched on.
I have temp wired the sockets into a non RCD protected way for tonight because of freezer etc. I appreciate there are faults there but just wondered how you guys would recommend going about testing and locating the faults.
I did quickly connect each leg of the ring separately to the MCB one leg trips straight away, the other trips after approx 5 seconds.
I am going back tomorrow and any help would be great - thanks.