tizbad

-
Joined
May 22, 2009
Messages
37
Reaction score
0
Location
cornwall
hi, i went to a friends house to swap a burnt out dimmer for standard switch ( 250w dimmer for 10 x 50w downlights). no probs. friend fones back few days later says rcd has tripped on 4 random occasions in 2 days since i swapped switch. went back earlier found downstairs light circuit had 0 Mohm between N - E, but rcd still holds. could not get rcd to trip with tester. took L, N and E on down light circuit out of board, rcd now tests fine, ramps out at 28mA + times all good. put bad circuit back in rcd no longer works, still holds.

house is 20 yrs old on a TT system and looks to have been wired by a incompetent diyer, 1 x 30mA main switch no bonding etc.

the install will be put right when friend returns from travels in new year, downstairs light circuit isolated from board, just cant work out why the rcd is behaving in this way.

thanks in advance to any replies
 
Okay. I`ll give it a whirl. TT. Under correct operational conditions the L, N & E are quite seperate within the installation. So far, so good :)
Carry out an RCD test downstream of the device.
What does the tester actually do - dumps some of the incoming line current to the CPCs.
So, even tho the impedance thru a TTs earthing system (thru the cpc, earthing conductor, down rod,then thru the mass of earth) back to the supply transformer will be huge compared to the Z of L/N, the Potential Difference between L & E is enough for current to flow & take the only path it knows - the one of least resistance.
Important to remember here, that the Neutral in our functional installation has been left out the loop. Its seperated from the PE - as it should be - but now its not carrying all the incoming Line current back out, cos its being leaked to earth...
Guess what, that ****es the RCD off, so it trips - just as we`d want it to.
However, as you stated, with the cct in question connected, you had 0 Mohms - a dead short between N & PE. For now lets not worry quite where, how or why - just that we know we`ve a path of negligible impedance between the two.
Now when the RCD tester leaks a bit to earth, what does that current want to do. It`ll jump to earth ok, cos its at a lower PD. But so is the Neutral. And now they`re interconnected within the installation. And the neutrals path back to the TX is one hell of alot less impeded than all that soil & stuff. So which way does it head? Not down the CPCs to the rod. No Sir. Straight down the Neutral conductors & back along the main to the centre tap, where it then heads back t`ther way along the Line.
So now we`ve basically got our Earth Loop path as; Line from trannny > thru L pole of RCCB > along R1 to RCD tester > which dumps it to the CPC > which is now interconnected to the Neutral > so fault current then heads back thru N pole of RCCB > back to TX (& not thru Ze)
The residual current device senses no apparent imbalance, so holds. Just as it should in the circumstances - it`s not faulty.
 
But we do still have a fault - a short between N & PE. With the test current removed, the cct will once again function. Not safely. And not reliably either. Because in this condition it`ll be susceptible to transients in the earthing system. And when a neighbours rod, in close proximity, dumps enough to earth, instead of heading thru the earth back to the centre tap, as its designed to, now its got the nice low ohm Neutral to piggyback...and the RCD won`t like that.
So it trips. The user closes the contacts again. The small reversed earth fault current it sensed is now attenuated, it holds once again. Until the next eddy heads back upstream...
 
Hopefully, that makes some sense of it for you mate.
Al
 
Tizbad. You may want to do a continuity test between N & E on the lighting circuit in question. I have a ring to sort out at some point which I found a fault on when doing a board change. When I did Insulation resistance between N & E tested at 0 Meg ohms but on continuity about 2500 Ohms between N & E. RCD currently holds but eventually it will start to trip. So could be you have an old cable somewhere gradually breaking down.
 

Reply to rcd troubles in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
687
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top