RCD type | on ElectriciansForums

Discuss RCD type in the Australia area at ElectriciansForums.net

E

eckersecker

[ElectriciansForums.net] RCD type

Came across the above RCD whilst working on a TT system. It had no indication of tripping currents on it. There was no main fuse so I need to record it's details including BS number. I tested it with a 30mA ramp test and it did not trip. So I fitted a 30 mA RCD to the shed supply I put in assuming I had discrimination. Any details would be much appreciated.
 
Looks like a VOELCB with the little yellow test button on it. Needs taking out as it probably doesn't work anymore.

Might even be an early ELCB.


BS 842 if memory serves.
 
Last edited by a moderator:
Yes reasonably! , if you push the button under the switch it trips, and a zs reading from the sockets in the house trips it, a no trip test does not. I took the lid off and there is a big copper coil inside.
 
Does trip , as stated above and by home owner. Not possible for me to take out as there is no fuse before it. It isolates the house before the meter. I think this is weird as if the owner is unscrupulous he could switch off and wire in stuff before the meter.
 
If there is and earth connection to this unit, then it's definitely a VOELCB, if not , then it's a very early ELCB. In both circumstances it should be removed, as this unit is well past it's useful life expectancy!!!
 
Last edited by a moderator:
Agree, a VOELCB, and I would not be leaving it in. What's the consumer unit arrangement? I would probably be covering the system with a new front end 100ma rcd, if the CU is as old as the VOELCB!
 
Either a VOELCB or a 300 / 500mA RCCD, both Crabtree units looked similar. You need to look if there’s an earth in and out of the unit inside the housing if there is it’s a VOELCB.
 

Reply to RCD type in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
690
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top