A domestic customer has MK dual RCD board #1 and another BG dual RCD board #2 in loft.
On testing, a couple of circuits (32a & 16a radials) on board #2 had high Earth fault loop impedance ( over 3 ohms for a socket radial). I know that the BG board (in the loft conversion) does not really need dual RCD but interestingly by bypassing its RCDs EFLI drops by 1.4 ohms.
Has anyone seen such high resistances in BG RCDs ?
Has anyone seen high EFLI readings with 2x RCDs covering a circuit ?
BG technical have admitted that only a handful of RCD's have shown high loop readings & that by having 2x RCDs covering a circuit would induce a current in the RCD coil.
I have not noticed, however, that 2x RCD's downstream of each other have ever caused high readings in the past....any experiences/ views on this are welcome.
On testing, a couple of circuits (32a & 16a radials) on board #2 had high Earth fault loop impedance ( over 3 ohms for a socket radial). I know that the BG board (in the loft conversion) does not really need dual RCD but interestingly by bypassing its RCDs EFLI drops by 1.4 ohms.
Has anyone seen such high resistances in BG RCDs ?
Has anyone seen high EFLI readings with 2x RCDs covering a circuit ?
BG technical have admitted that only a handful of RCD's have shown high loop readings & that by having 2x RCDs covering a circuit would induce a current in the RCD coil.
I have not noticed, however, that 2x RCD's downstream of each other have ever caused high readings in the past....any experiences/ views on this are welcome.