Hi All

I would like to ask if there is a right and wrong way of wiring an RCD / RCCB up. I was under the assumption that the supply was always wired into the top of an rcd / rccb, I thought that the monitoring coil that monitored the voltage was situated in the top of the rcd / rccb and that is why it had to be wired this way.

Can someone advise please as I test a large number of these and have become confused with the situation.

Bulby
 
As far as I know there is no universal answer and you would be better off checking the manufacturers instructions for any units you are concerned about.
Most RCDs will have a connection diagram printed on them which will help you out if present.

A normal RCD does not monitor voltage however, it basically compares current flowing through each pole by means of a transformer arrangement.
 
Hi All

I would like to ask if there is a right and wrong way of wiring an RCD / RCCB up. I was under the assumption that the supply was always wired into the top of an rcd / rccb, I thought that the monitoring coil that monitored the voltage was situated in the top of the rcd / rccb and that is why it had to be wired this way.

Can someone advise please as I test a large number of these and have become confused with the situation.

Bulby

Thanks for the reply, i have tested a few hundred and sometimkes it seems when they are wired with the supply in the bottom they will not trip on test but if you re wire them with the supply in the bottom they trip ever time on test, i just wanted to know if somewere there was a standard
 

Reply to Rcd wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
244
This thread can now be closed, as I seem to also have space in the box for the first switch. Revised diagram below. Thanks folks.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top