I've just carried out a periodic inspection on a building on an old RAF/USAF site. Commercial single story building.
Wiring system is around fifty years old run in a mix of trunking and steel conduit.
Three phase supply, TN-S from local transformer around fifty meters away, underground supply in a mix of trench and conduit.
Plant room has busbar system feeding this building and three supplies outgoing to other businesses the other side of the road.
No lightning or surge protection.
Ze 0.15 ohms, PFC of 3.7kA.
IR tests of cables all above 4.45 MegOhms.
All R1+R2 well within requirements, all sub 1 ohm.
Lighting, sockets, fire alarm and water heater supplies.
Installation in good condition, roughly 12 LED panel lights, and a couple of switched mode power supplies.
Chint TPNE board, all single phase circuits.
All dead tests passed easily.
As soon as I try to do Zs the RCBOs trip out, this is using the low current no trip setting on a Megger 1552. Works fine on a different installation as I've just tested mine at home so it's not the tester.
When doing time tests on the RCD part they trip before the test can be completed, basically as soon as the meter starts to inject current it trips out the RCD.
All are Chint 61009 30mA AC type RCBO, B curve, 16, 20 and 32 amp.
I have checked for earth leakage on the main earth, no AC current detected but I am getting six amps of DC.
Also getting six amps DC when the DB tails are clamped but there's nothing on the installation that can generate this much current, the with DB isolated I still get DC current on the main earth.
I'm unable to turn off the other outgoing supplies.
Other buildings near the transformer are an old ammo bunker, some mad bloke who does some radio stuff and has PV set up on his roof, but nothing big enough for this amount of current.
The customer did mention that there's a solar farm just around the corner. Could this solar farm be pumping DC back into the HV/LV networks and could this be the cause of this large amount of DC detected on the earth?
Wiring system is around fifty years old run in a mix of trunking and steel conduit.
Three phase supply, TN-S from local transformer around fifty meters away, underground supply in a mix of trench and conduit.
Plant room has busbar system feeding this building and three supplies outgoing to other businesses the other side of the road.
No lightning or surge protection.
Ze 0.15 ohms, PFC of 3.7kA.
IR tests of cables all above 4.45 MegOhms.
All R1+R2 well within requirements, all sub 1 ohm.
Lighting, sockets, fire alarm and water heater supplies.
Installation in good condition, roughly 12 LED panel lights, and a couple of switched mode power supplies.
Chint TPNE board, all single phase circuits.
All dead tests passed easily.
As soon as I try to do Zs the RCBOs trip out, this is using the low current no trip setting on a Megger 1552. Works fine on a different installation as I've just tested mine at home so it's not the tester.
When doing time tests on the RCD part they trip before the test can be completed, basically as soon as the meter starts to inject current it trips out the RCD.
All are Chint 61009 30mA AC type RCBO, B curve, 16, 20 and 32 amp.
I have checked for earth leakage on the main earth, no AC current detected but I am getting six amps of DC.
Also getting six amps DC when the DB tails are clamped but there's nothing on the installation that can generate this much current, the with DB isolated I still get DC current on the main earth.
I'm unable to turn off the other outgoing supplies.
Other buildings near the transformer are an old ammo bunker, some mad bloke who does some radio stuff and has PV set up on his roof, but nothing big enough for this amount of current.
The customer did mention that there's a solar farm just around the corner. Could this solar farm be pumping DC back into the HV/LV networks and could this be the cause of this large amount of DC detected on the earth?