hey, i was rung today by my dad to come and look at a glasswasher that is causing the main RCD incomer to trip every time it trys to cycle.
This glasswasher is in a pub, over the last 2 days the landlady said every time she tried to cycle the dishwasher it tripped all her pumps out. The glass washer powers up fine and fills with water everytime it tried to run a cycle tho it tripped the RCD on the fuseboard, its a really old fuse board didnt catch the name but im going bk tomorrow after work to investigate more. my thoughts was could it be the element that is nakard and causing this tripping? if not any ideas?
also the shower in the flat above the pub is causing tripping aswell. The fuseboard in the flat is a dual RCD split board, the shower switch has recently been changed and so has the shower as the last 1 was nakard. now this is the interesting part. when the shower switch is turned on it powers the shower no problem, then when you push the power button on the shower it causes the opposite rcd to trip not the 1 feeding the shower side. Ive not had any experience with split rcd boards being in the commercial side of things. and this 1 is baffling me a touch. now i havnt had the cover of the board off to see whats going on inside ill be doing that tomorrow on my return visit. i just thought id post on here to see if any of you have had similar situations of this. also to maybe save myself some time when going back tomorrow. i dont have full test equipment available either this is a favor for some1 so just trying to help out without it costing them a fortune.
is it a coincidence these are tripping together or could it be something further down the line?
you could wel, be right on the dishwasher. as for the shower, check that the neutral is in the correct neutral bar in the CU. and you really need an IR tester to proceed any further.
edit. paul.m is close to you if you get stuck.
that was my thoughts on the neutral but will have to check tomorrow. The board hasnt been installed too long and i know of the company that installed it, ill see what tomorrow brings though just after some possible pointers before i waste loads of time
What good would that do in a split board??
It would mean that only the shower would trip, and not half the circuits in the house.
To the OP, if you haven't taken the cover off then you can't be sure the shower is on that side. It won't be the first time someone has moved a circuit from one side to the other and not updated the schedule on the front of the board! Or is it obvious by the MCB size where the shower is?
Surely with a split load board, you would expect there to be a load almost constantly on each side of the board, with each side being monitored by a separate RCD. So if the N for the shower is put in the wrong side, then side A (with the shower MCB) would have less neutral current than Line current and side B would have more Neutral current than Line current. I thought RCDs detect an imbalance, regardless of whether it is the Line or Neutral has more current flowing than the other. If they only detect when there is less Neutral current than Line current (because the shower N is in the wrong side), then I would expect the shower side to trip, not the other one.
Or is this a split load board with RCD on one side only? Shower MCB on non-RCD side?
Reply to RCDs tripping in the Australia area at ElectriciansForums.net
Ok I’ll try this when I’m down
L
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...