Hi, I recently installed a new c/u and was talked into a MCG board by my local wholesalers (which won’t be happening again!!!).

The problem I have is that the rcds are adding 0.51 to my zs reading. It’s a tnc-s system with a 0.04 ze. If I do an r1+r2 on a lighting circuit for example its 0.93 but my zs is 1.44. I have replaced the rcds but still getting the same reading. It is definitely the rcds as I have done a loop test either side of the Rcds there is a difference of 0.51. My question is are these readings acceptable as the zs is still within the limits or do I replace the board? thanks
 
One thing i will say is never use MCG they are absolute crap. So long as your Zs is below the maximum permissible then leave them in.
 
TBH Tel I have never used them.

i've used 1. it had 3 decent N bars so was versatile and has a built in spirit level so even i could get it straight. good price as well. ÂŁ65 fully loaded.( 2 RCD+10 MCBs) inc. VAT.
 

Reply to Rcd's with High Resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top