Hi, I recently installed a new c/u and was talked into a MCG board by my local wholesalers (which won’t be happening again!!!).
The problem I have is that the rcds are adding 0.51 to my zs reading. It’s a tnc-s system with a 0.04 ze. If I do an r1+r2 on a lighting circuit for example its 0.93 but my zs is 1.44. I have replaced the rcds but still getting the same reading. It is definitely the rcds as I have done a loop test either side of the Rcds there is a difference of 0.51. My question is are these readings acceptable as the zs is still within the limits or do I replace the board? thanks
The problem I have is that the rcds are adding 0.51 to my zs reading. It’s a tnc-s system with a 0.04 ze. If I do an r1+r2 on a lighting circuit for example its 0.93 but my zs is 1.44. I have replaced the rcds but still getting the same reading. It is definitely the rcds as I have done a loop test either side of the Rcds there is a difference of 0.51. My question is are these readings acceptable as the zs is still within the limits or do I replace the board? thanks