I've tried searching but every time I hit the 'search' button, it takes me out of the forum!

Set up: 6-way consumer unit (changeover). 30mA rcd controlling 4 power (32+32+16+40) mcb's + 2 6a rcbo's for lighting.

I've done all the testing. Voltage 247v. Everything fine but....

Upon testing the RCD,it trips 10.2mA @ 1I, and 8.4mA @ 5I
And the rcbo's ... 18.2mA @ 1I and 18.1mA @ 5I

Can I have some help in understanding what's going on. I know it's the rcd/rcbo combination (cause I changed it all for a straight 6-way unit with ONE rcd and then the results were as expected I-30.2mA & 5I-6.9mA ...)

thanks,

Stewart
 
Im with m4tty here, i dont understand what question you are asking, you have shown us a set of results that have passed so what is the question, are you confused that the x5 results should be a fifth of the x1? this isnt the case and this rarely is the case, to pass it just has to trip within the specified times thats all, existing leakage, load, voltage etc will all play a small part as to the result but as long as they meet the regs then all is good.
 
Well there you are then, all safe and sound :)

Hmmm, yes I was confusing the mA with the mS lol ..... put it down to a hard day and refusing to think clearly! Shall just go off and write out 5,000 times - "I must not write in to forum when thinking like a plumber!" ..... 5,000 lines later...... sigh! that's better, I shall go and make myself a nice cup of tea :) :)
 

Reply to RCDs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top