Steve Flex
Hi All,
Anybody have any experience regarding a Heatrae Amptec 12Kw electric flow boiler with control timer. I have been asked to install the above along with a plumber friend. I have checked the demand on the installation,which is ok, as it will be pulling a good 50A when going. It will be a 10m run from the consumer unit to the airing cupboard. I have done the calculations and it will need to be run in 10mm. The thing is the installation guide dosen't mention a contactor, which I think is necessary. I am thinking a 6A mcb to run the timer via contactor, at least a 50A mcb to run the boiler via contactor. I haven't had much experience with contactors, any ideas? Oh, yeah and there is only one space left in the consumer unit!
Cheers
Anybody have any experience regarding a Heatrae Amptec 12Kw electric flow boiler with control timer. I have been asked to install the above along with a plumber friend. I have checked the demand on the installation,which is ok, as it will be pulling a good 50A when going. It will be a 10m run from the consumer unit to the airing cupboard. I have done the calculations and it will need to be run in 10mm. The thing is the installation guide dosen't mention a contactor, which I think is necessary. I am thinking a 6A mcb to run the timer via contactor, at least a 50A mcb to run the boiler via contactor. I haven't had much experience with contactors, any ideas? Oh, yeah and there is only one space left in the consumer unit!