Good day.
I have recently been involved in an EICR on a property with 15 DB's.

The average PFC appears as 90A and the average Ze is 2.9
The system is TN-S

I suspect there is an earth fault somewhere which would explain the Ze but why the PFC reading?

Each DB is isolated by a BS88 80A or 100A at distances ranging from 5m to 30m

Any ideas?
 
are you talking a bout Ze ( at the origin) or Zdb at each board? pefc will be possibly higher than expected due to parallel paths.
 
Average Ze ? are you on about Zdb ? Your PEFC sounds about right for an EFLI of 2.9 ohms. You can work it out with sums and that. Talking of sums, do your Zdb readings match with what you calculated from your continuity readings of the sub feeds ?
 
sorry not enough information for you...
The average was taken from the readings of all 15 boards.
Also, yes you are right all Ze should be Zdb.
Range of PEFC is from 88 to 90.
Zdb range is 2.8 to 3.0

Thank you for your information, I should have thought about it a bit more rather than just jumping straight on here. So used to getting far lower Ze and much high PFC on single board tests.
 
Average Ze ? are you on about Zdb ? Your PEFC sounds about right for an EFLI of 2.9 ohms. You can work it out with sums and that. Talking of sums, do your Zdb readings match with what you calculated from your continuity readings of the sub feeds ?

Thankyou. All the Zdb values do seem very high. As an example one Zdb reading is 2.7 where the calculation for a 30m run of 10mm 2 core SWA (using armour as earth) is 0.2 .
 
Thankyou. All the Zdb values do seem very high. As an example one Zdb reading is 2.7 where the calculation for a 30m run of 10mm 2 core SWA (using armour as earth) is 0.2 .

I hope there isn't any main bonding conductors being taken to this and the any other DB's that are being supplied with 2 core SWA cables, as the armouring will not have a sufficient CSA for compliance??

Apart from that, something is very wrong here with the values you are stating for the Zdb's of these DB's....
 

Reply to readings? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
404
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
993
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top