REALLY Low reading PFC Test | on ElectriciansForums

Discuss REALLY Low reading PFC Test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

riotmaster

On a caravan site, just tested the main incoming Ze and PFC.

Ze= 8.67Ohms, (TT System, so less than 21Ohms OK)

but PFC was 21AMPS??? as in 0.021kA

there are RCD's at different points throughout the installation, which keep tripping randomly.

also switching the shower lights on, was tripping the RCD for the Cafe (both on different DB's, only fed from same DB at origin but different ways)

Any thoughts or comments... I need some HELP?!
 
thanks for the quick response...

they are seperate buildings but next to each other.

and no shared earths, or borrowed neutrals... though thats only from a visual inspection, doing a periodic tommorow. they seem to all be back to relevant earth / neutral bars in the CU, and then obviously through the supplies back to incoming DB.
 
yeah i'm going to take another one with me tommorow. But considering he's having problems with tripping RCD's, i'm not presuming anything, whether it be a faulty tester, or purely a problem with the circuit, especially neutral/ earth arrangments.
 

Reply to REALLY Low reading PFC Test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top