R
Robo
Tnc-s install. with a ze of 0.31. Im gettin a high zs of 44.1 on kitchen lights. All lights have earth conected. Does this sound like a loose earth or faulty jb buried somewhere?? Iv repalced fuseboard and all bonding and earthing meet regs. I understand its RCD protected so ok but id like to get the reading down. Thanks
agree^^^^ as yet you don't know if it's R1 or R2 that's causing the high reading. could be a screw tigtened in the insulation, making a high resistance connection. also, make sure you haven't got a crossed polarity somewhere.
If the dead tests are good (low R1+R2 values) and the Ze is good but you still get high Zs readings it could be your meter playing up. I know on the 'no trip' loop tests noise on the supply can give you some right odd readings. Had this before and had to calculate Zs as the meter wouldn't give a accurate reading.