5 5.6Over-current protective device rating exceeds the current carrying capacity of the circuit, feeding multiple outlets / accessories. See Regulations 433.1.1; 533.2.
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem
 
Is that the only code that was given?

Seems simple enough to downgrade the ocpd just to solve this one issue.


"A full rewire" suggests there are other issues have been brought up where repair just isnt enough.

how old is this installation? how old is the fuseboard/ consumer unit?
 
5 5.6Over-current protective device rating exceeds the current carrying capacity of the circuit, feeding multiple outlets / accessories. See Regulations 433.1.1; 533.2.
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem
Unless you post the electric report with names, addresses etc redacted what you have posted is meaningless
 
Not necessarily, it might be that the OCPD is correct for the load and the circuit needs to be rewired because the cable is undersized.
thats not what was stated though... they say the ocpd exceeds the ccc of the circuit... which to me means the cable. Loads can be disconnected/ unplugged... Still leaves a ocpd bigger than the ccc.

Either way.... its not right and needs addressed..... but this one comment on an eicr on its own does not mean the whole place needs a FULL rewire..... (as OP says).... but maybe just this one circuit ??


We need a heck of a lot more information.
 

Reply to Received Electirc report and states in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Some of the points should have been picked up by previous people doing the testing. Sounds like this is a thorough report. Not everything is...
Replies
11
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
590
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
817
First one drove by , sucked his teeth , muttered under his breath 'ah looks okay from here'
Replies
21
Views
5K
On a much smaller scale, the idea of a busbar chamber.. You have a thick cable supplying the copper bars… then several smaller cables branching off.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top