Hi guys,

Here is the set up in a shop:

Three phase supply from the supply meter into escos. From the escos there is tails going to a 100A isolator which supplys a board upstairs and a set of tails supplying a 100A 100mA RCD. From the RCD into a distribution board downstairs. From this distribution board there is a cable supplying another board from a 63A Type C MCB.

The problem is that one of the machines in the shop tripped off during a cycle. It first took out a 40A MCB supplying it. I checked out the motor, compressor etc in the machine which were all sound. When turned back on it ran for a few hours and then took out the 63A MCB supplying the board. Im thinking that it is overloaded as there is four freezers, a cooker, four machines which have a total rating of around 62 A aswell as lights sockets off this board. It's funny thou because the shop was a new installation about three years ago and there has not been any previous problem. The owner says that there has not been any new equipment.

The system is a TT system.

I was thinking of getting another 100A isolator to supply the distribution board and doing away with the 63A MCB.

What would you recommend? Also why would the electrician who wired it have used a 100A 100mA RCD instead of A 100A 30mA?

Thanks:D
 
it sounds to me like a faulty machine ,motor breaking down underload ,or a faulty MCB ,as you have said its quite heavely loaded so perhaps the MCB's worn ,whats the total load if diversitys taken into account the 100ma was very common on TT systems in 15th edition but an update in the mid 80s made them non compliant :)
 
Last edited by a moderator:
The total load with diversity taken into account is around 40A. But there is times when all the machines run at the same time so to allow for this I was thinking maybe a Type D MCB. I was at the wholesalers today and asked if they had a 100A MCB (MEM) but apparently the biggest is 63 A.:rolleyes:
 
biggest problem with the D type is hitting the maximum ZS , may be an idea to use a clamp meter and check the loadings do you know what the supply fuses are because if they are 60 per phase its possible that you may blow one of them , its the its worked fine before that causes concern ,why has it just started tripping , realy it sounds to me like they need to use the three phase as if your loading up a single phase to 62 amps yu could be causing an inbalance on the other phases
 

Reply to Recommended Solutions in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
715
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top