recoomendation code for breaking capacity | on ElectriciansForums
Discuss recoomendation code for breaking capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
what is the recommendation code for a mcb rated at 1KA and the pfc on the installation is 1.8 ka
I might be being a bit thick here (has happened before, will happen again), but doesn't that mean that the MCB can't safely break more than 1KA and with a Pfc of 1.8KA you have a protective device which is incapable of safely interrupting a fault current?
The device upstream with the higher rated fault current will break. The MCB with the 1kA rating would then need to be replaced as it could have been damaged with the higher than rated fault current.
Reply to recoomendation code for breaking capacity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
i notice you mention "fire rated" instead of "metallic" Are we talking about a metal consumer unit? I know its presumed... but just checking