This is a page I wrote to help the people at work understand the reference method.
Hope its of some help to others
Reference methods for domestic installations
The reference method box on the EICR is there to indicate how the particular circuit is installed.
This then allows us to verify that the cable used is capable of carrying the current for that circuit.
A basic house with floor boards would have different reference methods for different circuits and also different methods for the same circuit.
A Twin and Earth may be run up a wall clipped in a cupboard from the CCU, then laid under the floor and down the wall in metal conduit in the wall to a cooker panel. This is 3 different types of run so looking in the regs we need to pick the one that has the greatest impact on the current carrying capacity of the cable.
The reference methods used specifically for flat twin and earth are these.
In our above example the cable runs clipped up the wall in a cupboard. This is reference Method C.
It then runs under the floor, this is Method, B, 100 or 101 depending on the presence of thermal insulation.
It then runs down in the conduit buried in the wall to the CCP this is Method B
I would use reference method 100 or 101 if there’s insulation as this is a worst case scenario. If there’s no insulation then I would use B.
Common Installation methods for domestic installations.
T&E installations see above
Method A
Method 103 reduces the current carrying capacity greater than A
101 and A are close to the same, But 101 is for T and E, Method A and 101 reduces the current carrying capacity greater than B.
Method B reduces the current carrying capacity greater than C.
Hope its of some help to others
Reference methods for domestic installations
The reference method box on the EICR is there to indicate how the particular circuit is installed.
This then allows us to verify that the cable used is capable of carrying the current for that circuit.
A basic house with floor boards would have different reference methods for different circuits and also different methods for the same circuit.
A Twin and Earth may be run up a wall clipped in a cupboard from the CCU, then laid under the floor and down the wall in metal conduit in the wall to a cooker panel. This is 3 different types of run so looking in the regs we need to pick the one that has the greatest impact on the current carrying capacity of the cable.
The reference methods used specifically for flat twin and earth are these.
- 100, under thermal insulation less than 100mm
- 101, under thermal insulation greater than 100mm
- 102, in a stud wall with cable at the edge’s and full of insulation
- 103, in a stud wall with cable running through the middle of the insulation.
In our above example the cable runs clipped up the wall in a cupboard. This is reference Method C.
It then runs under the floor, this is Method, B, 100 or 101 depending on the presence of thermal insulation.
It then runs down in the conduit buried in the wall to the CCP this is Method B
I would use reference method 100 or 101 if there’s insulation as this is a worst case scenario. If there’s no insulation then I would use B.
Common Installation methods for domestic installations.
T&E installations see above
Method A
- Singles or multi core cables run in a conduit buried in insulation
- Surface mini Trunking.
- Run under floor boards if NO insulation.
- Running down in or on a brick wall in conduit.
- Running down in cavity wall with no insulation. With or without conduit
- Clipped to a wall or ceiling.
- Buried direct in plaster.
- SWA running down wall.
- SWA buried in the ground.
Method 103 reduces the current carrying capacity greater than A
101 and A are close to the same, But 101 is for T and E, Method A and 101 reduces the current carrying capacity greater than B.
Method B reduces the current carrying capacity greater than C.