Ok, before I start I should say that I normally assume that 132.16 means that bonding and earthing should be ok before ANY additions or alterations take place. However I just wanted to explore what the reg actually means.
So....
"no addition or alteration.... shall be made... unless it has been ascertained that the rating and the conditionn of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate"
As I read this that means you are only concerned whether the earthing and bonding is ok for the addition, not the whole system.
So, lets take an example: Adding a socket spur to a ring at an existing socket where the Zs is say 0.8. Lets also say the Zs at the origin is 0.2.
Using those figures I get a PEFC for the installation of 1.15kA (ie. 230/0.2) and a PEFC at the modification of 287A (230/0.8).
So, assuming a 100A BS88-2 main fuse with a 1.15kA PEFC I get t = 0.4s ish and the adiabatic gives me main earthing conductor CSA = 6.3mm2 to protect the whole system.
However if I am only concerned about the addition then my PEFC is 287A through a 32A type B MCB giving me a CSA= 0.8mm2!!
So, leaving aside arguments about common sense and making sure the whole system is safe, if the customer refuses a earthing upgrade am I allowed to make this alteration and sign it off if say there is a 4mm2 earthing conductor present? Obviously with a note that there is a C2 fault on the cert!
This goes against what I thought was allowed so I am very interested to hear other views and why.....
So....
"no addition or alteration.... shall be made... unless it has been ascertained that the rating and the conditionn of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate"
As I read this that means you are only concerned whether the earthing and bonding is ok for the addition, not the whole system.
So, lets take an example: Adding a socket spur to a ring at an existing socket where the Zs is say 0.8. Lets also say the Zs at the origin is 0.2.
Using those figures I get a PEFC for the installation of 1.15kA (ie. 230/0.2) and a PEFC at the modification of 287A (230/0.8).
So, assuming a 100A BS88-2 main fuse with a 1.15kA PEFC I get t = 0.4s ish and the adiabatic gives me main earthing conductor CSA = 6.3mm2 to protect the whole system.
However if I am only concerned about the addition then my PEFC is 287A through a 32A type B MCB giving me a CSA= 0.8mm2!!
So, leaving aside arguments about common sense and making sure the whole system is safe, if the customer refuses a earthing upgrade am I allowed to make this alteration and sign it off if say there is a 4mm2 earthing conductor present? Obviously with a note that there is a C2 fault on the cert!
This goes against what I thought was allowed so I am very interested to hear other views and why.....