R
Rajan Shakti
how is contactor overload rating differs from its contact current rating
Discuss regarding contactor connection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The rating current of a contactor is the value of load the contactor can take safely. For instance a 25amp contactor can take safely a constant load of 25amp
An over load is set to the load taken by the device, normally a motor that this contactor supplies. So you 25amp contactor could be supplying a 5amp moter. The overload would be set accordingly and if the motor developed a fault as soon as the amps rose above the overload setting it would trip and dis-engage the contactor