In commercial electrical installation is it acceptable to run cables horizontally?
We need to relocate existing sockets and add new to this circuit.
Also if we can not achieve a depth of 50mm into wall does reg 522.6.101 apply if we use RCD's?
 
Leaving the subject of skilled or instructed person aside
The cable is not mechanically protected.its less than 50mm in the wall,it needs additional protection by rcd


quote
if we can not achieve a depth of 50mm into wall does reg 522.6.101 apply if we use RCD's

You are using the rcd "because" it does not comply with 522.6.101
 
You should be aware of cable zoning ...its a fundamental basic for any Electrician to know whether just out of college or 50yrs in the trade and the BS 7671 covers Domestic, Commercial and Industrial so same applies, refer to your Regs book or OSG to remind yourself of these zones ....as your still an apprentice ill soften up on you as we all start somewhere just curious as you put occupation Project Manager and your an apprentice Electrician ....you should have a competent person overlooking your job to answer such a question.
 
or, if you're a builder/kitchen fitter, just run them the shortest way, diagonal/behind door architraves/thrown behind cupboards.......
 
Was an apprentice some years ago. The situation applies to our electrical contractors on site and I am trying to defend their work. I have the buildings maintenance guy saying the wiring is a hazard because its not 50mm from face of wall and dangerous because its run horizontal. This guy is causing us grief with client. Any comments to defend the situation would help. Thanks
 


Any comments to defend the situation





If the cables run horizontal are in a safe zone,ie there is an accessory indicating the safe zone and additional protection (if needed)then he is a

Would "Pleb" be good enough?
[ElectriciansForums.net] regs for horizontal cabling
 
Easier to get him to show you where you are not complying with BS7671!!
Cables run horizontal that do not achieve a 50mm depth and are RCD protected will comply to the Reg's. As stated above, they do meet defined safe zone philosophy!!
 

Reply to regs for horizontal cabling in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
663
  • Sticky
I'm going to get the wording wrong because I am far too lazy to look it up. A previous version said 'must be followed' now says 'should be taken...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top