Just wanted to double check two regs.
1. Do you HAVE TO have a double pole switch between the cut out and the DB (so you can isolate the DB)
2. Do you HAVE TO have a 16mm earthing conductor alongside the 16mm tails (the load on the installation is no more than 5 amps ((teleco cabinet Virgin Media))
 
1. no.

2. earthing conductor should be sized to be able to carry PEFC without damage.
 
you must have a single point of isolation for the installation, but this can be the main switch of a DB or MCC, ir consumer unit. It doesnt have to be a standalone isolator, although in most cases that is preferable.
As far as im concerned no as long as the installation is not PME, you can size the earth as you would a CPC, that is either by calculation using the adiabatic or by selection from the BS7671 tables. The DNO may have caveats ect where they insist upon a minimum size of condcutor for the mains.

- - - Updated - - -

tel beat me!!
 
It is a PME installation ..... So 16mm earthing conductor ? What Virgin are saying is that if maintenance is ever needed to be carried out in the DB, the only way to isolate it is by pulling the main cut out fuse ...
 
It is a PME installation ..... So 16mm earthing conductor ? What Virgin are saying is that if maintenance is ever needed to be carried out in the DB, the only way to isolate it is by pulling the main cut out fuse ...

Well here is your chance to get Virgin to lobby the government for that isolator they wont be putting into the proposed smart meters

Virgin seem to be applying common sense,that will never do in this industry,but required to work on the board ? No
 

Reply to Regs on isolating a DB and earthing conductor size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
513
Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
198

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top