afaik, cables and non=electrical services should be installed so that either will not cause detriment to the other ( 528.3.4 bgb ). i have a gas fitter telling me that my SWA should be 250mm from his gas pipe. i need to hit him with a reg., preferably one that is more specific than the one quoted above. thanks, chaps.
 
found it. it's in the osg. which refers to BS6891:

BS 6891:2005 requires that electrical equipment be seperated from gas pipes by a minimum of 150mm and electrical cables by seperated from gas pipes by a minimum of 25mm.
 
Any help for ya? : Regulation 528.3.3 requires that where an electrical service is installed in proximity to a non-electrical service, it must be arranged so that any foreseeable operation carried out on the other service will not cause damage to the electrical service or the converse. This can be achieved by suitable spacing or mechanical or thermal shielding.
BS 6891:2005 Installation of low pressure gas pipework in domestic premises, clause 8.16.2 states that gas installation pipes must be spaced at least 150mm away from electricity meters, controls, electrical switches or sockets, distribution boards or consumer units. There should also be a separation between a supply or distribution cable of at least 25mm for domestic pipework up to 35mm or 50mm for piepwork over 35mm.


Sent from my iPhone using Tapatalk
 
If it's the gas regs then that concerns the placing of gas pipes in proximity to cables, not the other way round. Get him to move his pipes :D
trouble is that his pipes were there before me. DNO installed 3 external meter boxes with the bottoms 4" above his pipe. I then has to run 3 10mm SWA distribution cables in that 4" gap, which itself is only a foot above ground level. I'll find out on Sunday which went in first, the DNO boxes or his pipe.
 
It's meant to prevent damage when working on 1 or other service.

Tell him you can manage not to cut open a Gas pipe when working on cables, so he should be able not to set fire to your SWA with his blowlamp.

He wouldn't set fire to skirting board if it was only 25mm away.
Oh hang on........
 
the gas pipe was first, then the DNO fitted their meter boxes close above the pipe. just phone client and it looks like it's just a simple matter of redressing the cables to ensure the 25mm spacing.
 

Reply to regulation query. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top