433.2.2
The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434.
433.3.1
A device for protection against overload need not be provided:
(ii) for a conductor which, because of the characteristics of the load or the supply, is not likely to carry overload current, provided that the conductor is protected against fault current in accordance with the requirements of Section 434.
Would the following theoretical situation fulfil either of the above regulations, and if so which one?
100A main cut out fuse supplies an 80A switch fuse via 25mm tails.
After 80A SF, 25mm tails to henley block, where the tails split. 25mm to main house CU, and 10mm to garage CU.
The 10mm tails to the garage CU would not be protected from overload by the 80A SF, but would they be protected if the sum of the breakers in the garage CU totalled less that the current carrying capacity of said tails?
The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434.
433.3.1
A device for protection against overload need not be provided:
(ii) for a conductor which, because of the characteristics of the load or the supply, is not likely to carry overload current, provided that the conductor is protected against fault current in accordance with the requirements of Section 434.
Would the following theoretical situation fulfil either of the above regulations, and if so which one?
100A main cut out fuse supplies an 80A switch fuse via 25mm tails.
After 80A SF, 25mm tails to henley block, where the tails split. 25mm to main house CU, and 10mm to garage CU.
The 10mm tails to the garage CU would not be protected from overload by the 80A SF, but would they be protected if the sum of the breakers in the garage CU totalled less that the current carrying capacity of said tails?