Yep that's what I was thinking!It wouldn't need to be floor to ceiling trunking, but I could put it floor to ceiling to make it look a little better

Yep that's what I was thinking!It wouldn't need to be floor to ceiling trunking, but I could put it floor to ceiling to make it look a little better
You delaying my G&T! I see WPD charge £157.26 + vat, to provide a new isolator. Has your pal got the pennies?
Am I making a mountain out of a mole hill?
To fully comply with regulations I can leave existing tails in place if they fit, or replace tails to isolator using trunking if they don't?
For main earth can I run 10mm through the cavity to the connector block replaced for an earthing terminal?
Upgrade bonding, ensure cabling is safe and in good ordera and then change board.
You are overthinking this, if I was to assess the job and you had left the existing tails in place, upgraded earth and bonds to 10.0 I would not find a problem with it. I would definitely recommend separate rcbos though due to the limited amount of circuits.Am I making a mountain out of a mole hill?
To fully comply with regulations I can leave existing tails in place if they fit, or replace tails to isolator using trunking if they don't?
For main earth can I run 10mm through the cavity to the connector block replaced for an earthing terminal?
Upgrade bonding, ensure cabling is safe and in good ordera and then change board.
Agree but an assessor will use rule of thumb that the earthing conductor to the MET should be 16.0, then 10.0 to the CU as the circuit protection is provided by the 60A fuse.Seeing the meter box is recessed it is probably almost filling the cavity anyway, though it is not ideal the cable has to cross the cavity at some point, whether it does it diagonally or straight across is fairly immaterial and since it will be going upward to the CU any water that might (how)?) get in will drain away from the inside wall.
You can try and ring the DNO and ask about the earth being undersized but I would not hold out much hope, but worth a try. BE prepared to stay on hold for a while and have all the details to hand and be prepared for them to only want to talk to the customer (more likely for the supplier).
The 6mm would likely only be undersized because it is a TNCS (PME) supply and so the earth is also a bonding conductor and so needs to be a minimum of 10mm².
As just an earth it would probably meet the adiabatic equation requirements, but not the bonding limits.
Not disagreeing with you Richard at all just that the OP would need to be confident if the assessor queried why it wasn't 16.0, some of them only see things in black and white. Either way it needs changing as it is undersized to support the new bonding.The earthing conductor from cut out to MET is only required to be 16mm² when using the selection table and it is stated in the regulations that this is likely to provide oversized conductors, therefore using the adiabatic equation (in this case subject to the bonding requirements as well) is a better and more comprehensive design.
There is no decrease applicable from MET to CU because of the size of the switch fuse as it is the same size (probably) as the cut out fuse and in both cases would be overidden by the bonding requirements.
Don't make more work for yourself. Start the EIC (for the CU), include your other works in that. Show your assessor the EIC. When you've passed your assessment, and got your shiny badge, bin the paper EIC and use the Elecsa on-line forms to complete a new EIC. Then you can notify the BC through Elecsa when finalising your Elecsa EIC. Save a few treesI'll get all preliminary work completed and issue MWCs for the light changes and switch changes (not absolutely necessary but some more paperwork to show assessor).
Good start hope the rest is plain sailing also.Thought i'd leave an update regarding this. I phoned WPD this morning and told them their earth was inadequate, being 6mm on PME.
I was ready to fight to get a free upgrade however there was no need. The guy on phone said that's too small I'll get someone out to you today to assess.
40 Minutes later a chap turned up who looked at it and said definitely needed upgrading and he'll have it scheduled for tomorrow or Wednesday.
Result![]()