I am looking for a 240v 75-100 amp relay. To switch over from mains to generator for power.
The switched cables are 16mm2.
Does anyone know where to get one?
 
The way I would sort that is to use 2 contractors electrically interlocked or just a manual changeover switch.


Sent from my iPhone using Tapatalk
 
Thanks for the quick replay.
What I am looking for is when the mains power goes off (which it is doing all the time just now) I have the generator coming on automatically but I don’t want to be feeding power back down the line. But I want it to happen automatically as someone is not always there to change it manually.
 
Sounds like you need to invest in an automatic changeover panel to allow separation between the two supplies.


Sent from my iPhone using Tapatalk
 
You should really look at getting a proper ATS if your going to have a generator back up supply of that power. Most modern ATS unit have timer and sensors fitted to control the chage over period. Such as if the power goes off and is restore withing seconds it will avoid activating the switch over. It will idle the generator to balance it before it brings it fully on line. Then on resumption of power it will keep the generator running to ensure a steady supply before shutting down.
 
Agree with Sintra & Malcolm! You really need to be looking at an auto changeover panel with contactor interlocks. As malcolm says modern panels have phase failure devices and timers built into them to eliminate the risk of connection between your generator and the grid, and vice versa.

You really dont want to risk bringing your generator and the grid together!!
 

Reply to Relay 240v 75-100 amp in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I'm just trying to understand the current your suggested relay needs to handle. Surely the above is not the running current of the lamp? That...
Replies
2
Views
192
  • Question
Interesting document thanks. But it neglects the half-wave rectification, and also totally neglects the effect of the coil inductance when...
2
Replies
31
Views
2K
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
Thank you, both. Seems like common sense may have prevailed, and the fellow is indeed going for one of the modern mirrors you mentioned...
Replies
3
Views
201
  • Question
Yes you will need to install # 4 wiring times 4 for your 2 hots, 1 neutral and 1 equipment ground. As for keeping the grounds and neutrals...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks