skiandy

Hi I have been asked to quote for a supply to a remote electric gate only problem is we have calculated the cable run to be 500 meters from the supply. Does anyone have any advice please.
 
600watts / (400v x 1.732)
0.88Amps per phase.

If we assume a power factor of 0.85 then we have 1.01amps per phase.

Now that run is rather a large one, voltage drop allowance of %5 so 20v for 400v.

Usually a 1mm 3-phase cable would be fine for a 1.01amp load per phase, but with a 500m run you would have a voltage drop of 21.21v at MV/A/M of 42.0, just that little bit to much, so go with a 2.5csa cable to be safe, 3-phase N/E, thats a voltage drop of 8.5v, and so this is ok.

Id go for a 6amp 3-phase C curve MCB, 2.5 3-phase SWA cable.

Hope that helps.
 
Last edited by a moderator:
Thanks,

I pretty much agree with that.

What do you think the highest ambient temperature that the cable could reach in a summers day, just curious on this one.
 
I suppose in the UK around 35 degrees on an insane summers day brought about by global warming, if clipped direct onto a tray above ground.

The ambiet temp correction factor for 35 degrees would be 0.94

So for example if a 2.5 twin & earth had a current carrying capacity of 27A, with a correction factor of 0.94 it would go down like this.

27 x 0.94 = 25.38

Obviously thats the current carrying capacity for a twin & earth PVC cable, not an SWA, so dig out your on site guide for a more accurate result.

But either way the ambiet temperature wont be a problem if you install a 2.5 3-phase SWA cable to your motor.
 
Last edited by a moderator:

Reply to Remote Gate Supply in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
L
  • Article
Underground oil tank feed problem This unit is located in France where they use diesel not kerosene. The feed from the underground tank is not...
Replies
0
Views
156
LostinFrance
L
  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
2K
Have a chat with your local victron supplier, they do several units that will do just what you are wanting to do. limit the supply load to 5kw...
Replies
1
Views
677
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
147

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks