Morning guys,

I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds a sub-db to a small office. The sub-db is an old wylex rewireable db with 3 of the 4 ways used (Sockets,sockets,lights). My company does not want to replace the sub-db as there are plans of removing the offices in the future.

My plan is to supply the office DB with 6mm SWA and a B40 MCB from the DB I am replacing. Also, test all outgoing circuits of the office DB to ensure they are in a safe condition. Finally, I would note on the EIC about connecting to the existing board and the client is aware of the DB not meeting current regs.

My question is should I be installing a 40A RCBO instead of an MCB at the DB feeding the office sub-db, at least the sockets and lights would have RCD protection from the new DB that i'm installing? Or am I overthinking this?

Thanks in advance.
 
I would say you are overthinking it. If your not altering any part of the office installation, then leave it alone ust test the circuits fed from your new DB. Does the office DB have a up to date EICR?
Technically you should not use an mcb to feed a sub main as there will be no selectivity between the supply mcb and the fuses in the wylex board. Saying that I see it all the time, what you need to look at, is will it matter if you loose all power to the wylex board due to fault on one of the final circuits fed from it.
 
I would say you are overthinking it. If your not altering any part of the office installation, then leave it alone ust test the circuits fed from your new DB. Does the office DB have a up to date EICR?
Technically you should not use an mcb to feed a sub main as there will be no selectivity between the supply mcb and the fuses in the wylex board. Saying that I see it all the time, what you need to look at, is will it matter if you loose all power to the wylex board due to fault on one of the final circuit

Thanks for the reply.
Not altering any part of the office installation just supply new cable to the office DB.
Yes the office has a recent EICR (6 Months ago) All circuits passed Zs requirements.
Office DB is made up of 5A,15A and 30A circuits so I think 30A might trip me up on selectivity between 40A MCB and office DB. However, the office is basically redundant, which is why my company is not forthcoming about replacing office DB and bringing wiring up to current regs.
So loosing all power is not a big deal.
 
Unless those sockets are likely to power outdoor stuff, etc, I would not be too bothered. Though using an RCBO is easy and allows that aspect to be ticked off (assuming its not rammed full of leaky IT stuff).

As @Flanders says you get poor selectivity with a MCB up-stream. It can be OK for overload if you have 1.6:1 or more ratio, but once you have a fault above the instant trip point of the upstream MCB they will generally both fire. How important that is kind of depends on what it is used for and so likelihood of a fault and implications of whole sub-DB going off.

MCCB often are you choice here if budget allows, or a switched-fuse for single circuit so long as you have enough of a margin with down-stream MCB/RCBO. If you look in the better catalogues, such as the Hager commercial distribution one, they have tables near the back of selectivity limits for MCB/MCB and fuse/MCB cascades, etc.
 
Thanks for the reply.
Not altering any part of the office installation just supply new cable to the office DB.
Yes the office has a recent EICR (6 Months ago) All circuits passed Zs requirements.
Office DB is made up of 5A,15A and 30A circuits so I think 30A might trip me up on selectivity between 40A MCB and office DB. However, the office is basically redundant, which is why my company is not forthcoming about replacing office DB and bringing wiring up to current regs.
So loosing all power is not a big deal.
Ok so In this case I would not worry about selectivity. As you have a current EICR for the wylex DB and is not part of your alterations then I would just test up the wylex board. Compare zs at DB with EICR to confirm all final circuits from the wylex DB will disconnect under fault conditions ,job done
 

Reply to Replacement DB to Submain RCD advice in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
804
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top