E

easysushi

Guys,

I am going to be replacing a consumer unit as part of my NICEIC eval. Please can you answer the following for me.

What steps or tests are required before CU is changed ?

Do all circuits need to be re-tested R1+R2 ?
Do all circuits need to be re-tested for Insulation resistance ?

Any advice would be very much appreciated


Cheers


Ty
 
I dont R1R2 if it is only a CU change but do Zs all final circuits. As you are likely to be changing the type of protective device it will be neccessary to verify that the new protective devices will meet the required disconnection time. I also IR test the installation as a whole, only if the reading is low will I test circuits individually.....RCD test on completion and of course verify bonding etc.
 
Last edited by a moderator:
I have to say i do R1 R2 tests and ring continuity tests , IR tests then Zs , Thewn RCD tests , install bonding to services and change the bathroom lights if they are incorrect for zones , then check for any damaged sockets and switches and replace if damaged , at the end of the day its my name on the cert / notify
 
I have to say i do R1 R2 tests and ring continuity tests , IR tests then Zs , Thewn RCD tests , install bonding to services and change the bathroom lights if they are incorrect for zones , then check for any damaged sockets and switches and replace if damaged , at the end of the day its my name on the cert / notify

Yes,I do ring continuity tests...end to end at least....forgot to put that in my above post.
I'ts amazing how many 'rings' on a 30a fuse in the old DB turn out to be non rings when you test them. Best to find out before you stick them on a 32a mcb in the new DB.
 
I must admit i made that mistake years ago looked at a board counted circuits and fuse sizes then got a new board there wasnt a ring had to go out and get a bigger board and loads of16 amp mcb's , i have done the Zs tests and calculated the R1 R2 for the cert but it didnt feel right doing it , lol i know it sounds daft but i always learnt do the tests as the book then you cant go wrong
 
Basic premise should always be test everything both before (and fix any issues) and after the cu change. Otherwise how would you know whether you've introduced the problem or not?

Edit: If you take that a stage further and were working for a client. You change the cu and when testing find a problem that takes you two hours to fix how could you justify to the client the cost of fixing the problem (unless built into the quote of course).
 
Last edited:
Basic premise should always be test everything both before (and fix any issues) and after the cu change. Otherwise how would you know whether you've introduced the problem or not?

Edit: If you take that a stage further and were working for a client. You change the cu and when testing find a problem that takes you two hours to fix how could you justify to the client the cost of fixing the problem (unless built into the quote of course).


For what its worth, I agree with your thinking

Keep'em coming guys all this info is just what I'm looking for


Ty
 
Basic premise should always be test everything both before (and fix any issues) and after the cu change. Otherwise how would you know whether you've introduced the problem or not?

Edit: If you take that a stage further and were working for a client. You change the cu and when testing find a problem that takes you two hours to fix how could you justify to the client the cost of fixing the problem (unless built into the quote of course).

This discussion has been had on here before.
Personally I dont think it is practical to test everything before a CU change as it's likely the before CU change visit will be to quote.
Are you going to spend a couple of hours or more doing R1R2's,ring tests etc on a job you might not even get??
More often than not the CU you are going to change will be a right mess and next to impossible to work out correct neutrals and disconnect rings etc.
OK....in an ideal world yes....but in the real world an IR test is quick and simple and will give an instant idea of whether there is going to be any faults to rectify,but our quote will state that any faults found during the CU change will be rectified at extra cost.
 
do a PIR before cu change (sort ahy issues arising) change CU then do a full test R1R2 IR cpc continuity rings continuity Zs Ze rcds

Thats ok if the client is happy to pay and is definately going to have the work carried out by yourself, but I'll be ****** if I'm going to do a full PIR fpr **** all and then some other ****** does the job.:eek:
 
Thats ok if the client is happy to pay and is definately going to have the work carried out by yourself, but I'll be ****** if I'm going to do a full PIR fpr **** all and then some other ****** does the job.:eek:

If the customer doesnt pay up then Dont give them the test results. Then they will have to have it done again and again untill they do pay for it...
 

Reply to Replacing Consumer unit, What tests are required in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
137
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
928
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

My understanding is it's not necessary unless compromising a fire barrier. Hager instructions: Cable Access: Cable access into the metal...
    • Like
Replies
1
Views
195
Crimp or Wago inline connector, my preference would be Wago push fit...
Replies
1
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top