Hi
After a bit of advice:
I am just doing a bit of home testing prior to starting my 2391 later this month, but have come across a couple of strange results. Measured the R1 and got 0.98, also got the same for the Rn so not a bad start, but got 1.95 for the R2. I tested it a few times as I don't rate the Fluke crocodile clips, but got the same result. Cable is 2.5 so with 1.5 CPC expected 0.98 x 1.67 (1.63). I have checked for loose connections but all seems ok.? Then I joined the lines and neutrals (opposites) and measured at each socket. At the majority of sockets measured 48, which was fine 0.98+0.98/4 = 49. But on some double sockets one side measured 48, but other measured 97 or 98. Again I looked in the socket but no problems. Anybody any ideas? I know I could wait to my course starts, but really bugging me
After a bit of advice:
I am just doing a bit of home testing prior to starting my 2391 later this month, but have come across a couple of strange results. Measured the R1 and got 0.98, also got the same for the Rn so not a bad start, but got 1.95 for the R2. I tested it a few times as I don't rate the Fluke crocodile clips, but got the same result. Cable is 2.5 so with 1.5 CPC expected 0.98 x 1.67 (1.63). I have checked for loose connections but all seems ok.? Then I joined the lines and neutrals (opposites) and measured at each socket. At the majority of sockets measured 48, which was fine 0.98+0.98/4 = 49. But on some double sockets one side measured 48, but other measured 97 or 98. Again I looked in the socket but no problems. Anybody any ideas? I know I could wait to my course starts, but really bugging me