Hi, I've just been doing some practising on a smallish radial circuit with a few spurs.. just looking for some help to explain why when doing an IR test between L & N its reading 0.3Mohm but for L-E and N-E i'm getting over 500Mohm.

Ta
 
Copestake
Am I reading GN3 right when it says connect L&N together, testing to Earth?
This is an acceptable way of IR testing for an existing installation.

If you are going to test between L&N, may I suggest doing a 'soft test' @ 250V first.As this will then show if something is still connected (that you may have missed) without running the risk of damaging vunerable equipment, which if you do damage you will then be liable for repair or replacement
 
Last edited:

Reply to Resistance testing radial sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
677
davesparks
D
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top