resistance | on ElectriciansForums
Discuss resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
G
gavinrawls
I think im having a moment but what is the maximum resistance reading allowed in a continuity/polarity test ?
resistance is dependant on the overall length of the cable, you can calculate the length by calculation if you use the tables for resistance in the big green book appendixes.
when i was training on a board the resistances were 0.3ish what would sort of values would i expect in house?
It is an interesting point though.
The measured R1 with R2 or R1+R2 values are added to the Ze value for the supply to give a prospective calculated Zs value. This is then compared to 80% of the given maximum Zs values for a given size of protective device (MCB)
Reply to resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
M
Heat resistant paste?? Hi guys What do you guys use when having to solder close to plastics? Are the pastes any good or not? If so, what products...
macka09
M
Sold and on its way to the new owner.