Hi, I need some advice - I came across a customer who wants me to supply power to a wet cooker in a restaurant.
this "thing" has 3 burners and each burner is separate connected through 13A plug - factory fitted.
However each burner is 2.99 kW, so actually it's absolutely fine to use it on a 13A plug, but I'm looking for ideas how to supply it from fuse box as together it's still just under 9kw
because this is a restaurant - I'm afraid no diversity can be taken into calculation?
its ca 16 meters (cable length) from CU

do I really need to run 10mm cable to supply 3x single 13 A sockets / on 40A mcb?
sounds strange to me, but have no another idea now - so any advice appreciated
thanks
tom
 
Doesn't each appliance require a single point of isolation under the UK regs?
This is what I mean. But from other side - I can see it as a table with 3 separate burners fitted into it?
As this unit is already factory fitted with 3 x 13A plugs, it may be right to run it on 3 x 16A mcb?
 
6mm² 40A radial socket circuit, using sockets that can take 2 x 6mm² cable (I think MK and Crabtree are OK). method C. Plug in using the supplied plugs.

But running each socket from the same 40A breaker with individual 2.5mm² cables would be easier. The load is limited by the plug top 13A.
 
Thanks Richard, I haven't think about the limitation caused by 13A plug ;)

its always worth to ask on the forum - thanks everybody - my problem has been solved ;)
 
personally, i'd run 3 2.5mm cables, fed via a 3 phase 20A MCB , (input side commoned up) so that all 3 would isolate simultaneously for maintenance, then after a couple of weeks, when the plugs have welded themselves into the sockets, hard wire each into a 20A D/P switch. using this method. all 3 can be isolated by the MCB, or individually by the 20A switches.
 
whichever way you go, i'd ditch the plug/socket arrangement. lost count of the number of welded/melted plugs i've come across when drawing this level of load. once you get a bit of contact resistance it spirals up into heat, increased resistance... more heat....
 
whichever way you go, i'd ditch the plug/socket arrangement. lost count of the number of welded/melted plugs i've come across when drawing this level of load. once you get a bit of contact resistance it spirals up into heat, increased resistance... more heat....

That is good advice bearing in mind the length of time they will be operating .
 

Reply to Restaurant wet cooker wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
531

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top