ElectricEddie
With hindsight I can see how my previous thread and questions were utterly unthoughtout with regards to my design process and I thank admin for shutting it down, but the reason I have come on to here is for help as I have previously read through a bunch of threads on here and it seems as if it's full of knowledgeable people. As admin quite rightly pointed out I am inexperienced but I am extremely determined and believe it or not quite intelligent. :: And I am in the position where this installation is down to me so I need to make sure I do it right.
so I have been doing some thinking and calculations and I have realised that apart from being not properly protected the 16mm te + 16mm Earth combo was the incorrect cable choice and total overkill so I'd like to get that out the way straight away and I'll be pulling it out tomorrow.
now I have calculated the maximum demand for each of my sub main consumer units and because of the way that I have segregated them they will all be around the 35-40a mark apart from the kitchen one which will obvs be a bit higher due to having the cooker, washing machine etc on it I will calculate them 100% tomorrow on site.
according to the ccc chart and my method of installation 6mm/10mm swa will be sufficient dependant on the exact calculations (as it's sort of borderline at that ampage) to power each submain am I right in thinking then in that case that I could run those to a 4 way distribution board with a mains isolator on the incoming side and install each line conductor into a 40a(dependant on exact max load calcs) mcb and then use my split load boards for each of my final circuits which will be rcd protected.
I hope now this is a more sensible/professional properly calculated method and I welcome any constructive input/criticism.
thanks again
Ed
so I have been doing some thinking and calculations and I have realised that apart from being not properly protected the 16mm te + 16mm Earth combo was the incorrect cable choice and total overkill so I'd like to get that out the way straight away and I'll be pulling it out tomorrow.
now I have calculated the maximum demand for each of my sub main consumer units and because of the way that I have segregated them they will all be around the 35-40a mark apart from the kitchen one which will obvs be a bit higher due to having the cooker, washing machine etc on it I will calculate them 100% tomorrow on site.
according to the ccc chart and my method of installation 6mm/10mm swa will be sufficient dependant on the exact calculations (as it's sort of borderline at that ampage) to power each submain am I right in thinking then in that case that I could run those to a 4 way distribution board with a mains isolator on the incoming side and install each line conductor into a 40a(dependant on exact max load calcs) mcb and then use my split load boards for each of my final circuits which will be rcd protected.
I hope now this is a more sensible/professional properly calculated method and I welcome any constructive input/criticism.
thanks again
Ed