Hi all,

Just looking for opinions on a popular dispute between our guys.

Are the regulations retrospective?

By this i mean would you add to a ring main or install a socket without RCD protection?
Would you do the same with lights now as per new 18th edition?
If doing an EICR you see trunking up high which the cables come come loose in the event of a fire but do not fit clip as "it complied with a previous edition of the regulations"

This last statement is something i hear time and time again and it is something i totally dismiss. The regs are there to be followed.
 
The work you do has to comply with current regs. How you achieve this is up to you but it only pertains to the work being done and not any of the existing installation with the exception of fundamental requirements such as earthing and bonding.

When inspecting an older installation "it complied at time of install" has nowt to do with it. We inspect using the current standard against which to evaluate danger or potential danger.

References
introduction to BS7671
132.16
Section 621
 
I totally agree with both of the above points.

Some of the sparks i know would happily spur a new socket off a ring main which has rewireable fuses with no rcd protection and say the circuit complied with a previous edition wtf?

I think the new lighting reg is daft too but it is there regardless so am i right in saying that in future if changing a light the circuit has no rcd you should be installing one to additionally protect the circuit? Some of my guys are saying clients wont agree to that! A cheap job has just become an expensive job. I dont buy that answer at all the regs are there to be followed of not then what is the point?
 
The problem is, the public... they have no clue about the regulations and the IET (in my opinion at least) don't do enough to educate them.

So when you rock up, give a dam, and quote to do a compliant safe job you're going to be more expensive than Dangerous Dave who doesn't give a fig about little issues like no RCD protection or the earthing and bonding.
 
So when changing a light under the 18th edition and the lighting circuit has no RCD protection and the consumer unit has no room to instal said RCD, what are we to do? As said previously a cheap £25 light change job becomes “sorry, but you need a new £500+ consumer unit installed, because the circuit now requires RCD protection”, ‘oh thank you Mr Electrician, please turn this simple cheap job in to an expensive rip off job, just wait there while I go contact BBC Watchdog’.....
 
So when changing a light under the 18th edition and the lighting circuit has no RCD protection and the consumer unit has no room to instal said RCD, what are we to do? As said previously a cheap £25 light change job becomes “sorry, but you need a new £500+ consumer unit installed, because the circuit now requires RCD protection”, ‘oh thank you Mr Electrician, please turn this simple cheap job in to an expensive rip off job, just wait there while I go contact BBC Watchdog’.....

Or provide a stand alone RCD, or RCD FCU for a circuit alteration.

Changing a light fitting would not be a circuit alteration in my eyes.

I do agree it's a stupid new reg though.
 
Anything you install now should comply with the current regulations.

An EICR carried out now should be carried out to the current regulations, however you only report on items concerning safety, you don’t report on items which don’t comply but have no effect on safety.
For example the old colours don’t comply, but don’t effect the safety of the installation.
 
The work you do has to comply with current regs. How you achieve this is up to you but it only pertains to the work being done and not any of the existing installation with the exception of fundamental requirements such as earthing and bonding.

When inspecting an older installation "it complied at time of install" has nowt to do with it. We inspect using the current standard against which to evaluate danger or potential danger.

References
introduction to BS7671
132.16
Section 621
The work you do has to comply with current regs. How you achieve this is up to you but it only pertains to the work being done and not any of the existing installation with the exception of fundamental requirements such as earthing and bonding.

When inspecting an older installation "it complied at time of install" has nowt to do with it. We inspect using the current standard against which to evaluate danger or potential danger.

References
introduction to BS7671
132.16
Section 621


Is there anything in the bs7671 regs book itself that back this up. I agree with you in that the work carried out should comply but not necessarily back dated to the whole installation if you are only working on 1 circuit.

I've recently been roasted because of this and looking for some clarification to come back with if the subject arrises again.
 
Is it a ring main?

Seems a simple question to me? If ‘your guys’ can’t interpret simple Regs, maybe you need new ‘guys’ why are they arguing!?
 
Is it a ring main?

Seems a simple question to me? If ‘your guys’ can’t interpret simple Regs, maybe you need new ‘guys’ why are they arguing!?

No it was a new circuit out on the eve side of a splitload board so everything with the newly installed circuit was compliant. I was told that the other 4 lighting/other mcbs (not worked on) should have been replaced for rcbos to make them compliant even though they were never touched.
 
No it was a new circuit out on the eve side of a splitload board so everything with the newly installed circuit was compliant. I was told that the other 4 lighting/other mcbs (not worked on) should have been replaced for rcbos to make them compliant even though they were never touched.

Who told you that?
 
By my way of thinking that kind of standards he looking for would lead any electrician changing a socket front would have to replace a plastic consumer unit for a metal one because it's not up to current standards!!
 
I think the new lighting reg is daft too but it is there regardless so am i right in saying that in future if changing a light the circuit has no rcd you should be installing one to additionally protect the circuit? Some of my guys are saying clients wont agree to that! A cheap job has just become an expensive job. I dont buy that answer at all the regs are there to be followed of not then what is the point?
More expensive yes, but not necessarily hugely more expensive, you could put a rcd in an enclosure on top or next to the CU and route the light circuit through that. not a vastly difficult task. a cheap non high end branded RCD can be bought for under £20 and a suitable enclosure for not much more. similar for sockets, can use a rcd socket or spur where possible or put one at the CU.
 
Faced with being failed and a revisit I decided it was not in my own interests to do so today but was looking for some king of backup from the regs to argue the case in the future.

Email the NICEIC directly and ask them to confirm that if any circuit in an installation is altered then all other circuits that don't comply with the 18th must be updated so that they do.

I'm no 18th regs expert but I'm absolutely certain that they will not agree with the above.
 
There has been two or three threads over the last few months with inspectors quoting so called facts which have little or no substance to them.
 
Faced with being failed and a revisit I decided it was not in my own interests to do so today but was looking for some king of backup from the regs to argue the case in the future.

Get in touch stating exactly what you were told and ask for clarification that was not given to you at the time as to which regulations were not being complied with. Ask for this in writing.
 
We had our assessment a few weeks ago and the inspector who seemed a decent fella just seemed to want to push their wares on us, he only looked about 20 yrs old.
 
I totally agree with both of the above points.

Some of the sparks i know would happily spur a new socket off a ring main which has rewireable fuses with no rcd protection and say the circuit complied with a previous edition wtf?

I think the new lighting reg is daft too but it is there regardless so am i right in saying that in future if changing a light the circuit has no rcd you should be installing one to additionally protect the circuit? Some of my guys are saying clients wont agree to that! A cheap job has just become an expensive job. I dont buy that answer at all the regs are there to be followed of not then what is the point?

I think it is lighting circuit that needs RCD protection, not the light fittings themselves. So changing a light fitting or switch would be fine, but if you added new lights then you would need to install an RCD
 
One thing that stums me is when, like today, I do an EICR on a house that has a 50+ old installation and I'm meant to judge it on the regs of the time it was done - How am I meant to know the regs at the time it was done? It's older than me lol!
 
One thing that stums me is when, like today, I do an EICR on a house that has a 50+ old installation and I'm meant to judge it on the regs of the time it was done - How am I meant to know the regs at the time it was done? It's older than me lol!

You're not meant to judge it like that, you use the current version of BS7671 for an inspection on any installation.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Retrospective Regulations
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
28

Thread Tags

Advert

Thread statistics

Created
ThrownRazor25,
Last reply from
Andy78,
Replies
28
Views
7,564

Advert

Back
Top