W

wilkyduch

Im looking for an overview on 3 phase power transmission and would be grateful if someone could answer this;
Does the current originating from an ac generator at the power station eventually return to the generator star point . Im confused because Ive read that the return path for current is to earth, in which case if correct then how would a circuit be maintained. Im under the impression that the intention of directing current to earth tis to get rid of it .Also if it is to the star point, what happens to the current when it reaches here.
 
Im looking for an overview on 3 phase power transmission and would be grateful if someone could answer this;
Does the current originating from an ac generator at the power station eventually return to the generator star point . Im confused because Ive read that the return path for current is to earth, in which case if correct then how would a circuit be maintained. Im under the impression that the intention of directing current to earth tis to get rid of it .Also if it is to the star point, what happens to the current when it reaches here.

Correct me if I am wrong but current always returns via the neutral and through the star point where it then travels back through the line in a constant loop. Unless there is an earth fault and in that event it will travel back to earth to the supply transformer. earth is connected to the star point so current will always travel in a loop through the star point back to the line.

I could be wrong.
 
Last edited by a moderator:
Correct me if I am wrong but current always returns via the neutral and through the star point where it then travels back through the line in a constant loop. Unless there is an earth fault and in that event it will travel back to earth to the supply transformer. earth is connected to the star point so current will always travel in a loop through the star point back to the line.

I could be wrong.

You're not. ;)
 
Do you mean with reference to the neutral, and howcome you can have balanced three phase systems when you believe that the neutral is required for the circuit to be complete?
 
Keeping it simple, ....It's the return path for single phase loads and unbalanced 3 phase loads....
Not so simple is when you start talking about ''odd order Harmonic currents'' ...They don't dissipate, they remain circulating at the supply transformer!!
 
In a balanced 3-phase load there is no current flow through neutral. A 3-phase motor works quite happily with out one. Whatever current flows out through red will return via yellow and blue in a very simplistic view of it. Only when you get un-balanced loads do you get any current flow in the neutral.
 
No expert by any means but OP mentions transmission rather than distribution. This is going to be at high voltage 400kV or 132kV and be to delta connected transformer so no need for a neutral as the balanced current will be zero. Think it will only be at distribution substations, where you will get a secondary connected in star, that you will have a neutral connected to the star point. :)
 
you need to sit down and listen to your heart, trust me it works! then be impulsive & take a risk.


You need to get a proper job or a life and stop posting rubbish just to promote your china dropshipping.. That is probably a scam since you've been kicked off three time I know of and not getting the message
 

Reply to return path confusion in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
  • Question
Check with your DNO as they will have a few questions. in theory no technical obstacles but we are not quite there yet with a clear agreed process.
Replies
4
Views
2K
  • Question
The DNO have been out this morning and said that the connection is PME, and both the braid and wire together are part of the system. They've...
Replies
24
Views
7K
Hi, My probe was on the outgoing neutral of the RCBO. I will be testing again this week so I will play around, many thanks for your reply.
Replies
7
Views
4K
  • Question
Soldering is the normal and preferred method of connection to lead. There is no reason for soldering to cause corrosion if done properly - the...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks