Reusing old shower circuit to supply bathroom electrics?
Hi everyone, hope you’re all doing well.
So this is potential plan,
Working on the property and there is a consumer unit with all RCBO’s,
But the entire lighting for the three bedroomed house is on one RCBO.
Going to be installing new spotlights (downlights), LED mirror and new extractor fan to bathroom. Ideal situation to give segregation of circuits would be to have the bathroom on its own circuit, so they’re not plunged into darkness if there is a fault anywhere in the house.
The consumer unit is a Siemens and have scoured absolutely everywhere and unable to find a 6amp RCBO for these for a new circuit .
So...
The shower circuit is now redundant, so considering using this to supply the bathroom.
Currently a 6mm cable on 32A
Type A Rcbo, Would bring the end of the 6mm cable down into a SFCU, And fuse down at 3 A ( So then cover my extractor fan as per manufacturers instructions) continue all my other wiring from there . Technically the 6mm cable is protected by the 32 amp RCBO and my 1.5 mil cable will be protected by the 3amp at the SFCU, So this all seems feasible and gives me segregation for the lighting.
I know in an ideal situation a new circuit would be run in 1.5, but as I’m unable to source a suitable RCBO this seems like the best alternative rather than putting all the bathroom lighting on the same lighting circuit.
I would label the board up accordingly,
Just to confirm the 6mm supply has tested out fine .
Opinions, thoughts and agreements and disagreements please,
thanks in advance
Hi everyone, hope you’re all doing well.
So this is potential plan,
Working on the property and there is a consumer unit with all RCBO’s,
But the entire lighting for the three bedroomed house is on one RCBO.
Going to be installing new spotlights (downlights), LED mirror and new extractor fan to bathroom. Ideal situation to give segregation of circuits would be to have the bathroom on its own circuit, so they’re not plunged into darkness if there is a fault anywhere in the house.
The consumer unit is a Siemens and have scoured absolutely everywhere and unable to find a 6amp RCBO for these for a new circuit .
So...
The shower circuit is now redundant, so considering using this to supply the bathroom.
Currently a 6mm cable on 32A
Type A Rcbo, Would bring the end of the 6mm cable down into a SFCU, And fuse down at 3 A ( So then cover my extractor fan as per manufacturers instructions) continue all my other wiring from there . Technically the 6mm cable is protected by the 32 amp RCBO and my 1.5 mil cable will be protected by the 3amp at the SFCU, So this all seems feasible and gives me segregation for the lighting.
I know in an ideal situation a new circuit would be run in 1.5, but as I’m unable to source a suitable RCBO this seems like the best alternative rather than putting all the bathroom lighting on the same lighting circuit.
I would label the board up accordingly,
Just to confirm the 6mm supply has tested out fine .
Opinions, thoughts and agreements and disagreements please,
thanks in advance