Hi folks been asked by a customer is possible to wire his industrial shredder so that it could reverse as well as go forward? Due to it becoming jammed frequently, it a three phase and neutral supply and help much appreciated.:D
 
Hi folks been asked by a customer is possible to wire his industrial shredder so that it could reverse as well as go forward? Due to it becoming jammed frequently, it a three phase and neutral supply and help much appreciated.:D

Hi markssparky,

I assume there is a contactor for the motor in it. You'll need a second contactor, wired with any two of the three phase swopped over, electrically interlocked with the original contactor. Add a selector switch
which selects one of the two contactors. If the circuit is star/delta then it is a bit more complicated as you need two star delta starters, one for forward, one for reverse.;)

Have you got a circuit diagram which you could post?
 
Hi markssparky,

I assume there is a contactor for the motor in it. You'll need a second contactor, wired with any two of the three phase swopped over, electrically interlocked with the original contactor. Add a selector switch
which selects one of the two contactors. If the circuit is star/delta then it is a bit more complicated as you need two star delta starters, one for forward, one for reverse.;)

Have you got a circuit diagram which you could post?

And mechanically interlocked as well
 
I wire these alot and due to the motors stopping with material in them its very easy for them to trip on startup unfortunately it requires a bit of a complicated set-up, the machine should start in reverse to clear itself before going forward so just a timer controlled inverter signal or contactor control, then current monitoring for jamming during run cycle to self clear with auto reverse depending on material in the feed (conveyor or hopper) needs to stop during these reverse periods etc etc....... as you see things can soon get very complicated, plc control , duel channel safety relays due to the hazard nature and fully self diagnosing system should all negate the need for manual reverse.
Some or all may apply to your job but you also need to consider rundown time for motor to coast to stop and that the reverse isnt active until motor is stationary as the interlocks on a forward reverse contactor wouldnt stop you trying to run it backwards straight away after hitting stop button even though the motor was still near full speed but coasting down.
Please remember that if you install a reverse system its down to you to safety access the machine , avoid reverse signal on forward rundown etc etc and any mechanical or electrical issues that arise due to your inexperience may land on your lap, which can be expensive if dealing with 75kw motors like i do.
Sorry to seem harsh but having a drive shaft snap can cause high maintenance costs or even serious injury if not worse.
 
Last edited:
I know nothing about shredders, but I would have thought that altering the wiring, saftey systems, or design of a piece of kit like this would be foolhardy at least, and perhaps criminal. Although it may cost a fortune, I should think he would be best speaking to the manufacturer, or at least someone familiar with the install and maintenance of shredders.

All IMHO of course;)
 

Reply to Reverse shredder in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
834
That won't solve the problem, you have a TNCS supply with a Ze which has gone out of spec for an unknown reason. You need to get the DNO or...
Replies
24
Views
4K
davesparks
D
Hi guys I’m at one of the funny times in my career where I can’t decide on what I want to do. I’m wondering if one of you experiences folks can...
Replies
0
Views
492
I was doing remedials from another contractors EICR, they had recommended that the 315A fuses feeding the powelocks be changed for 200A due to the...
Replies
15
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks