Revision Help | on ElectriciansForums
Discuss Revision Help in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
R
R.Beck
Hi, Im currently studying for C&G 2330 Level 3 - Installation. Currently Revising and will be getting stuck on some questions and would like help, so if people could answer them and help me when im stuck i woukll greatly appreciate it.
Here are some questions im stuck on.(Ill add more to this post more than likely)
1. A Low Resistance Ohm Meter is belived to be giving incorrect readings. State:-
- A) Two Methods which could be used to verify the accuracy of the instrument
- B)The Action To Be taken if the meter is found to be incorrect.
2.Each of the following protective devices , typical installation or load type, Were would the be used?
-A) Type Bcircuit breaker to BS EN 60898
B) BS 88 gG Cartridge Fuse
C) BS 1361 type II
D) Type C Circuit breaker to BS EN 60898
E) Bs 88gM Cartridge Fuse
F) RCD to BS EN 61009
C) BS 1361 type II
1) a) Test it on a known source / check box /
b) Have it calibrated
2) a) Domestic
d) Office /Industrial Banks of Flourescent Lighting (Inductive)
f) Domestic Cct RCBO
Not much help but its a start and others will probably add / correct me
Upvote 0
C) BS 1361 type II
2a domestic ring final circuit/radial circuit/lighting circuit
2d and e motor circuits
2b high pfc
Upvote 0
Brilliant. Thanks alot :)
I have 2 more questions now also haha ^^
1) Lets say we have a 6 may consumer unit with 5 circuits connected and the 6th left as a spare. we then carry out an insulation resistance test and get results.
i.e circuit: 1-10M Ohm, 2-20M Ohm,3-30M Ohm, 4-40 M Ohm,5-50 M Ohm,6-0M Ohm(spare).
To calculate the overall value of the insulation resistance if all circuits were tested would i just Add them and divide by 6? (10+20+30+40+50+0)/6 = Overall Insulation Resistance.
2) Identify 3 possible faults while carrying out a visual inspection prior to commissioning an installation on
a) a pendant type luminaire with 3 plate wiring.
b) a consumer unit (distribution board)
Im presuming for 2B that would include wireing in wrong order(forgot what the fault is called) were you put MCBs out of order(largest closest to main switch) - Can someone just tell me if that would be one.
Thankyou ^_^
Upvote 0
I would have thought mcbs in the wrong order would be bad practice only these days with split boards,
NICEIC wired our house up couple of years ago and largest is other side of the board and sizes work down towards main switch, if that is true does anyone know the reg for it.
Visual faults could be
Wrong size earth cable
Loose connections
Wrong mcb used ie 32amp on lighting circuit
Return part of ring circuit not connected
Chris
Upvote 0
Dont think its a reg just best practice
Upvote 0
No mate to work out resistors in parallel you have to do following
1/10 + 1/20 + 1/30 + 1/40 + 1/50 =
0.1 + 0.05 + 0.033 + 0.025 + 0.02 = 0.228
1/0.228 = 4.39 MegOhms
Correct me if im wrong anybody cheers
Upvote 0
the question could be worded wrong . i came across a question to find the unknown R
1/Requv = 1/R1 + 1/R2 + 1/R3 + 1/R4 + 1/Runknown
therefore
Runknown = 1/1Requiv - 1/R1 - 1/R2 - 1/R3 - 1/R4
Upvote 0
Yeah it may just be best practise, ill look it up tomorrow like Thanks alot for help people :)
And oh yeah it is just resistant isn't it, abit silly by me there. you people are gods at this ;) i'll give everyone thanks tomorrow :) by then i would probably have more questions!
Upvote 0
You are correct mate.
10 x 20 x 30 x 40 x 50 = 12000000
10/12000000 = 1200000
20/12000000 = 600000
30/12000000 = 400000
40/12000000 = 300000
50/12000000 = 240000
1200000 + 600000 + 400000 + 300000 + 240000 / 12000000 (then swap it over)
12000000 / 1200000 + 600000 + 400000 + 300000 + 240000
= 4.38Mohms
Upvote 0
Reply to Revision Help in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Electrical Courses