Revision Question | on ElectriciansForums
Discuss Revision Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
C
cfcsi
Just going through a few revision questions and this one popped up:
Q: An isolator in a 3 phase four wire system must disconnect
1. The 3 phase and neutral
2. The 3 phase only
3. The 3 phases , nuetral and earth
4. The neutral only
They give the answer as 2.
I would have said 1. -
Can someone explain the given answer???
Cheers
The clue is in the question; an isolator in a 3 phase 4 wire system.
It doesn't state where this isloator is or what it is controlling, the cable could therefore be the supply to a TN-C(-S) system.
If you look in section 537; specifically 537.1.2 "PEN conductors shall not be isolated or switched"
Upvote 0
Hi there,
Read it today in the OSG page 33.
'for a 3 phase supply to an installation forming part of a TT system,an isolator must interrupt the line and neutral conductors.In an TN-S or TN-C-S system only the line conductors need to be interrupted'
Cheers
Upvote 0
Reply to Revision Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Electrical Courses