Testing a RFC today. End-End values spot on: 0.19/0.21/0.34. All IR tests good bar N1-CPC2 which was 0.0 mega ohms.
N2-CPC2 was >299 mega ohms.
Why, if I am getting 0.21 and 0.34 on the end-end am I not getting 0.0 m ohms on both neutrals?
Is it to do with the resolution of my meter (MFT1552) for the different tests....I am guessing that IR tests are nowhere near continuity tests in terms of the resolution for each type of test.......me confused, though doesn't take much!
Please take pity on my frazzled brain!