First visit here so hi everyone.

My problem is I have just gone to do add a few sockets for someone and upgrade the fuse board. Done some basic checks first and discovered an existing ring main had a very high zs (3.4). Checked the Ze and was fine (.2 for tns). Assumed there would be a dodgy earth at one of the sockets but all earths seemed fine. Decided to check the R1R2 and there is only one earth cable at the board.

This is an old bungalow and the ring circuit consists of stranded live and neutral but the earth is run as a radial circuit from the board. I can't connect the outgoing live to incoming earth and vice versa so what do you do in this case? Am i getting odd readings because the earth isn't a ring? I just thought i'd see if there was an obvious explanation before i crawled in the loft to follow the earth.

Thanks
 
Thanks everyone. Got to the bottom of it. The plumbers had been in the week before and almost completely broke the earth in 2 when they fitted some pipes. All sorted now thanks
 

Reply to ri/r2 weird in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top