geffg

hi everyone. new to this. just carrying out a pir on a pub, and when looking at the d/b wiring, the neutrals/cpc etc dont marry up to the breakers. on the pir can i just limit doing a ring final test and code it or will have to persevere and find the right cables. as its a pub up and running i cant just disconnect cpc's etc. thanks for any comments
 
Note it on the cert that neutrals in the DB cannot be matched to the corresponding mcb's for testing purposes...(code 4). Carry out end to end tests at a socket outlet on the ring,not strictly correct but the results will be the same.
 
Note it on the cert that neutrals in the DB cannot be matched to the corresponding mcb's for testing purposes...(code 4). Carry out end to end tests at a socket outlet on the ring,not strictly correct but the results will be the same.

Personally I would opt for a recommendation code 2 if they can't be identified.
 

Reply to ring circuit determination in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top