Hey there,
Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52.
My question is I had a fault which I couldn’t find or rectify during a periodic test that I carried out yesterday (tenant property) occupied.
Circuit: Ground Floor Socket
32A Ring (r1 0.42, rn 16, r2 0.71)
R2 0.42 x 1.67 = 0.701 = Good above apart from rn!
Whipped all sockets off and checked connections at db of course. Couldn’t find anything at this point. Checked all points. Last thing was left was lifting floor boards. I couldn’t find anything in between (JB, interconnection, joint) I’ve asked tenant, unfortunately no relevant answer for an indication.
Carried out a long lead test CU - rn one leg (T&E) walked around - found dead leg from one point to the next that was giving 16ohms. Point A-B.
Split ring x2 radials (20A x 2 protective devices)
Carried out the procedural
Test R1/R2
R1/RN
Confirmed polarity….
Now getting voltage fluctuations and getting some sockets working and some aren’t due to not having 230VAC at every point on “Ground Floor Socket”
I believe there could be another dead leg or broken neutral, loose or lost.
Advice people? What would you?
How would you go about it?
Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52.
My question is I had a fault which I couldn’t find or rectify during a periodic test that I carried out yesterday (tenant property) occupied.
Circuit: Ground Floor Socket
32A Ring (r1 0.42, rn 16, r2 0.71)
R2 0.42 x 1.67 = 0.701 = Good above apart from rn!
Whipped all sockets off and checked connections at db of course. Couldn’t find anything at this point. Checked all points. Last thing was left was lifting floor boards. I couldn’t find anything in between (JB, interconnection, joint) I’ve asked tenant, unfortunately no relevant answer for an indication.
Carried out a long lead test CU - rn one leg (T&E) walked around - found dead leg from one point to the next that was giving 16ohms. Point A-B.
Split ring x2 radials (20A x 2 protective devices)
Carried out the procedural
Test R1/R2
R1/RN
Confirmed polarity….
Now getting voltage fluctuations and getting some sockets working and some aren’t due to not having 230VAC at every point on “Ground Floor Socket”
I believe there could be another dead leg or broken neutral, loose or lost.
Advice people? What would you?
How would you go about it?