Sorry to ask such a basic question. I want to surface wire a 13A ring circuit using 2.5 sqmm T&E in PVC mini trunking. If I run 2 cables in the same trunking to a socket , I note that the de-rating factor for two cables bunched is 0.8, which gives 23 x 0.8 = 18.4 A - i.e. below the required 20A. Do I have to use two separate lengths of trunking spaced apart (which wouldn't look too good) or is there a neater way around this? What is the "standard" way of dealing with this situation.
 
How many sockets are you running on the ring,how long will the run be:confused:Hi and welcome to the forum:D

Thanks for the welcome. There will be four double sockets on the ring. The total length of cable in the ring, including vertical drops, would be about 40 metres. The situation I am concerned about (2 cables in mini trunking) would exist at all four vertical drops (about 1.8 metres each) plus about 5 metres of horizontal run.
 
Can't see a problem with that,both cables will be fine in PVC mini trunking.I would still use a 32A RCD/RCBO at the board.
 
Last edited by a moderator:
I see I am not alone in wondering about this subject. It has been discussed before in another forum

IET Forums - Correction for grouping (Cg)


I think the conclusion is that because both the up and down legs are unlikely to be fully loaded at 20A, the theoretical 18.5A rating obtained by applying the grouping factor Cg is not something that one needs to worry about.
 
Last edited by a moderator:

Reply to Ring Circuit in Mini Trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
744
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
807

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top