just want to tell you about a fault i had to fix yesterday.
I was doing a periodic report and when i did the ring final test it showed
a line to earth fault. Old wylex board no rcd. After a few hours of breaking the ring down i found that a screw was touching the line conductor only in a concrete wall. So you might ask how then can there be a line earth fault.
What i discovered was the wall was damp and so the dampness was acting as a conductor carrying current to the nearest earthed metal
socket box in the concrete wall thus giving the earth line fault.
Im quite new to this game and was chuffed to find the fault:d