m25maintenance

just want to tell you about a fault i had to fix yesterday.
I was doing a periodic report and when i did the ring final test it showed
a line to earth fault. Old wylex board no rcd. After a few hours of breaking the ring down i found that a screw was touching the line conductor only in a concrete wall. So you might ask how then can there be a line earth fault.

What i discovered was the wall was damp and so the dampness was acting as a conductor carrying current to the nearest earthed metal
socket box in the concrete wall thus giving the earth line fault.

Im quite new to this game and was chuffed to find the fault:d​
 
i had one like that well nearly ,used to work in castles doing the maintainance ,cables were embeded in the joints of the rock covered in cement ,not right realy but with the restrictions of what you could do to install the cables ,very wet and dark lights , one day they lost the lights would stay on for 10 mins then trip the breaker , imagin a castle big walking along the passage ways found the whole wall was live ,hair standing up not because of the haunting past ,lol , could here a slight crackling withing the wall ,yep the cable had burnt out behind the cement and was arching ,so i know how you feel finding a fault like that ,nice one:)
 

Reply to ring circuit line earth fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
521
Very technical :D
    • Like
Replies
9
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top